SimonH Posted May 2, 2022 Report Share Posted May 2, 2022 Is it possible to replace the MCB’s on the betspack 4 with rcbo so I can feed the rack with an mcb and any fault will trip just the faulty circuit rather than the entire rack? being an outdoor venue gives us a little problem with rain!! thanks Quote Link to comment Share on other sites More sharing options...
kgallen Posted May 2, 2022 Report Share Posted May 2, 2022 Not sure how RCBOs, even on the mains side of the triacs, will play with dimming. I realise you might be talking about the hot power sockets but the MCB is common on the channel. I doubt Zero88 would support this modification to their product (if nothing else it would invalidate the formal product qualification they have to do for CE/UKCA marking). 1 Quote Link to comment Share on other sites More sharing options...
Edward Z88 Posted May 3, 2022 Report Share Posted May 3, 2022 Hi Simon, Hope you're well. 22 hours ago, SimonH said: Is it possible to replace the MCB’s on the betspack 4 with rcbo so I can feed the rack with an mcb and any fault will trip just the faulty circuit rather than the entire rack? 21 hours ago, kgallen said: I doubt Zero88 would support this modification to their product As per @kgallen's comments, this is not something that we can support. The only channel protection options for Betapack 4s are MCBs. You would need to look at Chilli Pro Bypass cabinets for RCBO protection per dimmed/hot channel. Edward Quote Edward Smith Product Specialist Email Support Link to comment Share on other sites More sharing options...
Recommended Posts
Join the conversation
You can post now and register later. If you have an account, sign in now to post with your account.