Hi Everyone,

Sorry if this is in the wrong section wasn't sure it this needed to go in Power or Discontinued Products.

 

My question relates to Chilli Jr Dimmers (6 Channel Install Dimmers) and if the below is just normal operation. As we have received a set of four of them for an install which were taken out of a dead venue a year ago and i wasn't sure if this was normal behaviour for them? We have never really seem this product before as much of the installs around here have always been Beta Packs or the bigger Chilli Dimmers.

When we attach a 650w fixture to any of the outlets we get a lamp glow not too noticeable but enough to see have the stage, looks around the 5% mark.

The Desk is not sending any values to the DMX Address and on checking our outputs DMX1-6 are all showing 0 value to the channel and All the preheats are off on all 6 channels and it appears this occurs on all four dimmers and all six channels. We have done the factory reset and restored back to factory settings, So starting to think this is normal operations unless this range used to have issues with burning out resistors?

I notice in the manual there is a min load per channel of 26w (0.1amps) is this just normal operation for this range of products or is this a fault that can be repaired?

I know this is a very old product as it looks like it was discontinued at least 10 years ago but any help would be appreciated as i would rather reuse these dimmers then send them to scrap.

Thanks in advance

Link to comment
Share on other sites

on these there are ramp adjust pots on the back of the keypad PCB, it sounds like these may be set to high.

the way we set them on the bench when building the units was turn preheat on and adjust until you get between 11-12v ac showing on the output.

PM me for more details.

 

Regards,

 

Keith Rogers

keith.rogers@signify.com

DD: +44 (0) 1633 833 101.

Link to comment
Share on other sites

On 12/2/2020 at 10:44 AM, KWR88 said:

on these there are ramp adjust pots on the back of the keypad PCB, it sounds like these may be set to high.

the way we set them on the bench when building the units was turn preheat on and adjust until you get between 11-12v ac showing on the output.

PM me for more details.

 

Hi Keith,

You were spot on it was the Three Ramp pot VR's on the back being set a bit too high. They were showing 7V at 0% and on preheat on they were showing 25-30v. Just adjusted them and they are back in line and working perfectly now. Thank you for the help :)

  • Like 1
Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...

Important Information

We have placed cookies on your device to help make this website better. You can adjust your cookie settings, otherwise we'll assume you're okay to continue.