The analogue 8 pin DIN connectors on the back of the console will control 6 channels, using a 0 to +10v signal. 

This information can be found on Page 35 of the manual, attached to the article below...

http://support.zero88.com/975532281

I believe Strand ACT6 dimmers have the ability to switch between receiving a 0 to +10v signal or 0 to -10v signal, so ensure this is set to receive a positive voltage. You’ll then be able to connect the console and dimmer together, and have intensity control of the dimmer channels.

Pulsar dimmers are usually wired differently, so I would recommend consulting your Pulsar dimmer’s Manual to determine the control pinout.

Lightmaster consoles use the following Output pinout...

Pins 1-6 are channels 1-6

Pin 7 supply voltage from the dimmer  

Pin 8 is Ground

Hope this helps, if you have any queries let me know. 

Edward

Edward Smith
Product Specialist

Link to comment
Share on other sites

On 4/11/2019 at 9:48 AM, Edward- Z88 said:

I believe Strand ACT6 dimmers have the ability to switch between receiving a 0 to +10v signal or 0 to -10v signal.

That is true of "newer" ACT6s however early Strand equipment (including ACT6 models from the 1980s to early 1990's) had a fixed 0 to -10V control signal. This requires an "inversion" circuit to change the 0 to +10V to 0 to -10V control voltage.

This link discusses such a circuit for Strand dimmers using 0 to -10V control voltage, if you are capable of some straightforward low-voltage electronics construction:

https://sound-au.com/project90.htm

(The circuit shown is for 2 channels. Note the need for a power supply to provide +/- 15V too).

Also regards the pinout of the DIN8, Zero88 and Strand use the same pinout - pins 1-6 are channels 1-6, pin 7 is a desk supply (output on a dimmer, input on a desk), and pin 8 is 0V/GND. Don't connect pin 7 unless you know it's the correct voltage for the desk. For example Betapacks output +20V (switchable to -20V) but the ACT6 may output -15V which would be useful to power your inverter circuit above.

Pulsar (and Zero88/Strand) pinout here: https://www.blue-room.org.uk/index.php?showtopic=27209&view=findpost&p=228788

 

Kevin

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...

Important Information

We have placed cookies on your device to help make this website better. You can adjust your cookie settings, otherwise we'll assume you're okay to continue.